MPPT 100/30 Zero Solar watts, 0.01 Solar Volts 0.0 Amps

Current set up: 22FT 2018 Airstream

100/30 w built in Bluetooth connected (+) to hot bus bar with 10 amp inline fuse and (-) to neutral bus

1 - 115 watt Zamp Solar

1 Interstate SRM 24 12v wet battery

This is the image from the app.

Controller shows blinking "Bulk" indicator light

When I plug in the panels, I see an increase in the Battery Voltage (tells me the panels are providing some energy to the controller)

When I engage the battery switch, I see a minor reduction in Battery Voltage

As I turn lights, radio fans etc on/off there is fluctuation in the battery Voltage

What I have not seen in any change in is Solar Watt, Voltage or Current.


Where have I gone wrong or is this simply how the system operates?




MPPT Controllers
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

Sounds like a wiring problem, do you have pictures of the wiring?

0 Likes 0 ·
anni-ka avatar image anni-ka commented ·
Hey,

Could you Tell me how you solved your problem? Because I have the same. Right after I plugged in my PV, the mppt tells me that I have 0.01v and no watts. The Batterie is all good.

Thanks :)

0 Likes 0 ·
Show more comments
1 Answer
lag323 avatar image
lag323 answered ·

Problem solved. In line fuse on Zamp panel was loose. All systems working and readings are within normal limits.