Hi All,
Scenario as follows. Grid attached Solar PV (SMA 3kw) installed 12 years ago. Quattro ESS system recently installed. Testing Grid failure when batteries are full and excess PV being generated. What should happen?
My understanding is that the SMA inverter was configured as grid attached (correctly) when it was installed i.e. frequency shifting will not work. This cannot be changed since my system has a bypass switch for the Quattro so the SMA inverter must always be configured as 'grid attached'.
What appeared to actually happen was the system tried to frequency shift (per the ESS parameters) and the SMA inverter noted the frequency was outside the acceptable 'grid-attached' range and decided the grid was faulty and stopped inverting. A few minutes later (i think there is a minimum wait time in the SMA config) , the system had restored normal frequency and the SMA inverter restarted. This cycle repeated many times - it did avoid overheating the system (not least because eventually somehow it caused the PV RCD trip). So, was this just lucky? I've seen other forum entries for similar scenarios where systems have overheated and shut down.
Colin