question

rpgilbert1 avatar image
rpgilbert1 asked

Does the AC Output #2 shut off on the Multiplus 2 24/3000/70 like on the Multiplus?

AC Output #2 on the Multiplus 24/3000/70 shuts off when the batteries are charging. We are using the Multiplus in an off grid system for household power. It doesn't appear that can be changed. Does this apply to the Multiplus 2 or is AC Output #2 hot continuously as is #1?

ac out 2
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·
  • AC-out-2

    A second output is available that disconnects its load in the event of battery operation. On these terminals, equipment is connected that may only operate if AC voltage is available on AC-in-1, e.g. an electric boiler or an air conditioner. The load on AC-out-2 is disconnected immediately when the MultiPlus-II switches to battery operation. After AC power becomes available on AC-in-1, the load on AC-out-2 will be reconnected with a delay of approximately 2 minutes. This to allow a genset to stabilise.


Though, with the programmable relay assistant you can override this behaviour (not done it myself) but if you search for this topic on the forum, you will find many posts on the subject.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rpgilbert1 avatar image rpgilbert1 commented ·
So the override is available for the Multiplus (1) as well?
0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic