I am putting together a dual phase system using 2x 48/10000 Multiplus II for a client who is supplied 3 phase from grid, but only uses 2 of the phases. When commissioning, what phase angle would be required?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am putting together a dual phase system using 2x 48/10000 Multiplus II for a client who is supplied 3 phase from grid, but only uses 2 of the phases. When commissioning, what phase angle would be required?
It could be 120 or 240 depending on which phases feed which Multi. and their phase relationship. You might check the phases with an oscilloscope.