GX-less Multiplus II with support from the Grid doesn't work as expected.

I just completed a Multiplus-II 5000/48 installation.

The grid is on AC-in, while all loads are on AC1-out. The MPII is connected to a DC BUS, where two SmartSolars and a bunch of LFP batteries are also connected. There is no GX device on the installation, for now.

The goal is to be able to use all available solar production (4kWp installed) and have the grid as support, for when the solar production is slim. Since there is no GX device, smart shunt, nor can-connected batteries, I have adjusted "DC input" voltages accordingly in "Inverter Settings", so as to not run down the batteries excessively.

However, it seems like this setup doesn't work exactly the way I want it to: Starting up the MPII with no AC-in works fine, however as soon as AC-in is electrified, the MPII goes into "Passthrough" mode and inverting stops, hence not using any of the solar production.

Only way I was able to make it work (kind of) the way I want, is to fiddle with the "AC Input Control" settings, in which case my loads are being fed by either the inverter, or the grid. I was aiming for true parallel feed from inverter and the grid at the same time.

I suspect that I will be able to make more adjustments if I put a GX Cerbo into the mix, but I was hoping I could set it up as originally intended without one. Is there something I miss? Some secret setting, or a jumper cable I missed somehow during installation?

Multiplus-IIESSsolargrid parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
shaneyake avatar image
shaneyake answered ·

You need to be running ESS and this requires a GX Device. The whole victron system is built around a GX like the Cerbo so I don't know why you wouldn't have one.

Please have a look at the Manual.
https://www.victronenergy.com/media/pg/Energy_Storage_System/en/ess-introduction---features.html

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thanar avatar image thanar commented ·

So, with no GX device, there is no way to make the system work as expected? i.e. power the loads from both inverter and the grid?

0 Likes 0 ·
shaneyake avatar image shaneyake thanar commented ·
There are workarounds like using Power Assist and Input current limit as you described but that is all you can do without a GX. You need a GX for what you are trying to do.


What country are you in? As ESS my require permission from your utility.

0 Likes 0 ·
thanar avatar image thanar shaneyake commented ·

Unfortunately, "Power Assist" and "Input current limit" work in exactly the opposite way that I need; they prioritise the grid.

I am in Greece, and feed-in is prohibited for the time being. That's why for now I decided to go with no GX unit, since I really don't need all the additional calibration offered by the ESS environment.