Unexplained voltage drop on VE.Bus - MultiPlus-II 12/3000/120-50


1673236289925.png


MultiPlus-II 12/3000/120-50 (Firmware 497) powered by shore-power AC as the only energy source. There is a constant AC load about 1.3KW, absolutely no load on DC bus, two battery banks are completely OFF (battery switches are in OFF position and disconnected from VE.Bus). Which means that the MultiPlus-II is the only DC source on VE.Bus.

What can cause the voltage drops as per above screenshot? I only noticed it because from time to time it drops below configured "DC input low shut-down" of 12.4V triggering Low Battery Alarm.

How to approach and troubleshoot this?

Thank you!

Multiplus-IIVE.Bus
1673236289925.png (332.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

All Victron devices are designed to always have a battery connected. Running the system without a battery is not supported and can/will cause problems.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bonsys avatar image bonsys commented ·
Thank you Matthias, do you mean incorrect system experience or potential Multiplus damage?