Hi I have just removed a Mutliplus 48/5000 from and site a Upgraded/installed a Multiplus II 48/5000
The latest firmware has been installed 459
The CCGX is displaying a resting voltage of 51.5
my two volt meters plus the BMS show the voltage as 53.5
it seems the Multiplus II has a incorrect voltage reading and is showing a way to low a reading
Note Charging has been turned OFF by the VE-BMS as I charge these to 3.5 volts per cell then let them drop to 80% SOC before charging is turned on again
is there a calibration available to adjust this anywhere ?????
I have tested the voltage AT the Multiplus II terminals 53.5 and the batteries themselves also 53.5
The Old multiplus 48/5000 voltage readings we all correct
assistants and other info
Gen flag is used set ignore AC1
AC sensor installed
ESS is installed with Grid Tie Inverter 5Kw
Relay on
Relay off
Panels installed are 4.5 KW
only AC coupled
Battery bank 20Kw Lithium Phosphate
Any suggestions