Will 24/3000 Multiplus still allow a/c passthru ?

Will 24/3000 Multiplus still allow a/c passthru if they have input power supplied to a/c in and are set to power assist mode where they only start inverting when large loads are applied if they are set to AES search mode to consume less power. The majority of the time they just sit there waiting till a large load is applied. The a/c in is from a Conext 4024 inverter. Each inverter are on their own separate battery banks.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

If AC in is present and sufficient, power assist will not kick in.

AES governs behaviour when AC in not available. This can mean a short delay before a new load is serviced from the battery.