220a Battery protect only worked once

I installed the BP with program 8a.

It worked once only shutting off at 12v and restarting at 13v but now let's the batteries go below 12v without cutting off.

Do I need to reset every time it activates?

Battery Protect
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·
What is connected to the output of the BP?
0 Likes 0 ·
Show more comments
1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

The BP is not designed for reverse current and you should not connect an inverter directly to it, that can damage the BP.
See manual:
https://www.victronenergy.com/media/pg/BatteryProtect_12V_24V/en/installation-and-wiring-examples/warning-when-connecting-inverters-and-inverters-chargers.html