Hi to the community!
We want to build a split phase system 240/240V 60Hz (located in Panama) with Victron Quattros of at least 30kW.
My question is which Quattros I should choose and if an Autotransformer makes sense.
I have to explain what the system should be able to do:
We want to run a wooden dry chamber (theoretic maximum of 20kW) consists of different devices. Most of the time its should not exceed 13kW, but theoretical 20kW are possible for a short term. All devices are 240V/60Hz
Furthermore there will be a small carpenter workshop, with different machines. The machines (all of them are 240V) in the workshop won’t run at the same time. The maximum of one machine is 4kW on 240V.
For the 120V will be the light and maybe small tools like a drill machine, but again, not many machines at the same time. So I think, not more than 1200W.
Initially we wanted to take two of the 15kW Quattros split phase (30kW) but I noticed in the beginning that the 15kW model is only in 240V available. (Later on I noticed in the manual that it is possible to order a model 15kW with 120V, I have to find out if I can get this model).
So I have three options for the topology:
1. Suppose I get the 15kW model with 120V, I would have two of them as a split phase system. I don’t think that I run into a balancing troubles (between the 120V phases), because the heavy loads run on 240V.
2. If I don’t get the Quattro 15kW 120V model, I have to take 4 of the Quattro 8kW models. Two in parallel and split phase. So I would have 32kW power at the maximum. Of course more expensive and more work with AC cable wiring!
3. Suppose I take two of the 15kW 240V Quattros and I will use a Victron Autotransformer (100A) and still most of the most loads are 240V, will the Autotransformer be the right solution? I mean, the Autotransformer makes it possible to use the 240V Quattros and is balancing the two 120V phases (if I understand the function of an Autotransformer in the right way).
The rest of the system (beside the inverters) will be the following:
- 55 kWP module power with a few MPPT RS (I have to do the calculation with the Victron Excel, if I have the data sheet of the modules)
- 176kWh LiFePo4 batteries (15 pieces in parallel with 48V/230Ah connected with copper busbar)
- Lynx system, Cerbo, all connected via VE.Can
- ESS, the system should be capable to feedback electricity if the dry chamber/workshop is not used
- A generator (have to think about the size) if there is a power outage and the batteries will deplete
I am a technical engineer and I build up a three phase system in Austria (3x220/50Hz) with 3xMultis 5kW, 15kWP and a self built LiFePo4 battery (560Ah@48V). So I am new to split phase and electricity in general here in America.