question

mswoboda avatar image
mswoboda asked

LiFePo4 4batteries in parallel

Hi,

I want to use LifePo4 batteries in parallel.
I will use a Chinese model which are able to "talk" to VE.Can bus. I think they are using the Pyontech protocol.

Suppose I will use 5 batteries with 48V and 230Ah and the BMS can handle 200A charge and discharge.
So the question is: What is the maximum Amperage I can charge and discharge with 5 batteries in parallel?

Kirchhoffs law says that the current is reduced in a parallel circuit:
As all batteries will be parallel, theoretical I could use 5x200A = 1000A, but in reality its too much, isn't it?


One company gave me a formula:
n...number of batteries
n x 200A / 2 = Max A

This would be 5 x 200 / 2 = 500A

What is the experience of the community?

I am happy with any answer!




Lithium BatteryBMScharge current limit48v battery
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@mswoboda

Check you can run 5 in parallel. Alot of batteries can't.

But in theory you have "enough" amperage to run a 45kVa load depending on your current share in the set up.

How are you wiring it up? To a bus bar individually or looping them?

0 Likes 0 ·
mswoboda avatar image mswoboda Alexandra ♦ commented ·
I will use Lynx.

You can use 15 batteries in parallel, thats what the producer confirmed.
The question is: What is the maximum of Ampere I can charge and discharge e.g. with 5 batteries (each battery has a BMS up to 200A).
The load of kW is a different thing. This has also to do with the inverters. But thats a different topic.


0 Likes 0 ·
mswoboda avatar image mswoboda Alexandra ♦ commented ·
...or did you mean busbars between the batteries?

At the moment I plan to connect each battery with cables.


0 Likes 0 ·
1 Answer
mswoboda avatar image
mswoboda answered ·

I think in the meanwhile I know the answer. Its better to build a busbar. Otherwise the batteries outside will be more used as the inner ones.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.