Temp x Cerbo temp sensors


We have a customer who has recent installed 4 x Cerbo temp sensors to part number ass000001000
the customer has everything installed and has lengthen the wires on 2 units. All four units are testing 10 degree hotter thank measured on the lug.

1 x temp sensor on battery bank
1 x temp sensor battery room
1 x temp sensor fridge
1 x temp sensor freezer.

Have you seen this problem? Can you shed any light or why this may be occurring? Is there a known solution for this issue?

Kind regards

cerbo gxoffgridTemperature Sensor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

Tried the search function?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@Donald Freer

A commonly asked question for sure.

You need to calibrate them by changing the offset. It mentioned in the Cerbo manual.

To do that you need super user access.