Hi Victron hive. Why do I get two different values for generator kWh in system overview and consumption on the VRM?, and if the AC input & output are not used, why are they shown? TIA :)
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi Victron hive. Why do I get two different values for generator kWh in system overview and consumption on the VRM?, and if the AC input & output are not used, why are they shown? TIA :)
Consumption tab shows energy used direct to loads
The system overview shows the total drawn from the generator, so includes battery charging and loads.
Thanks Alexandra, so in system Overview the Generator figure = Consumption + From Battery from the Consumption view? if so why do the values not equal the same?
Do you know why the AC in & out are shown in Overview when they are not needed?
It is something that is being worked on. What makes sense to some does not for others.
consumption direct to loads AC in house - 10kWh - your generator provided 53kWh.
So 43kWh went to battery charging.
Hi @Stad,
Some time in the very near future a new generator menu item will be launched in VRM and should answer your question.