Hi!
Is it possible to connect a grid-inverter to AC-Out 2 on the Multiplus?
My idea is to save the EM24 compared to connenct the inverter on AC-In.
(Multi is measuring the currents but kick the inverter out if grid lost)
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi!
Is it possible to connect a grid-inverter to AC-Out 2 on the Multiplus?
My idea is to save the EM24 compared to connenct the inverter on AC-In.
(Multi is measuring the currents but kick the inverter out if grid lost)
Yes, you can have a PV inverter on the AC-OUT but I would still have that inverter configured for frequency shift limiting.
All rules still apply.
https://www.victronenergy.com/live/ac_coupling:start
so, no need for frequency shift MG50 grid code or 1:1 rule.
Its not connected, if Grid fails.
Its basically the same as if it would be connected to AC-in.
Only differences:
- no EM24 needed
- AC-Out2 does come back with some delay time after AC-in.
- And, if coupled to AC-Out 2, you need to consider AC Passthrough power limitations also.
Can you explain why I need to consider AC PAssthrough if I want this in my setup?
I do not understand why I need that.
For what is worth: The Victron (48/5000VA/70) has it's own breaker of C32 and appropriate cabling. The PV is 3000W max output. When the grid fails the PV inverter shutsdown.
I know that the PV inverter is looking at the Hertz for shifting and disconnects when needed but when the grid fails it's shuts down. The grid is stable enough so I do not need to charge when the grid fails.
AC-coupling and the Factor 1.0 rule