Multiplus mounting above Pylontech L2 battery racks

I want to mount my 3 phase Multiplus II system above 4 Pylontech L2 racks placed at a wall. But following the user manual, the Multiplus should not be mounted over the batteries. Is this also valid for the totally encapsulated Pylontech L2 racks in a good ventilated room of about 10m2?



Multiplus-IIPylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
marekp avatar image
marekp answered ·

@Jupp

There is no problem in placing Pylontechs or any other LFP batteries under the inverters. You cannot place there lead acid batteries because they emit hydrogen during charging.

2 |3000