Manual says 90mm per + and - connections. There are two connections for each. Does this mean 2 x 90mm for + and 2 x 90mm for - ??
Thanks in advance
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Manual says 90mm per + and - connections. There are two connections for each. Does this mean 2 x 90mm for + and 2 x 90mm for - ??
Thanks in advance
total 90mm2, so 2x 50mm2 is also good.
Rule of thumb (very short or long cables excluded)
current / 3 = mm2
so a 3000VA unit at 12 volt can draw about 300A continuous max, / 3 = 100mm2 --> 90mm2 is fine.
that rule of thumb is for preventing too much heat in the cables.
for longer cable runs you calculate with the maximum voltage drop to prevent to much losses.