question

Robert Boerescu avatar image
Robert Boerescu asked

Fronius PV point as AC IN

Hey everyone,

I have a fronius symo gen 24 AC coupled inverter and a Victron easy solar 2 which I use only on one phase as backup power for some critical loads. There is no integration between these two. Easy solar mppt has four panels. Fronius 14 panels. I was wondering if I can put the fronius pv point output which comes up only as a backup solution giving up to 3kw power when AC grid goes out and there is sun as a AC in for Victron using an automatic transfer switch. The solution will be like this: when grid goes out, Fronius output to the grid goes out, victron ac in from grid goes out, Fronius pv point comes up in max 90 sec if there is sun and gives up to 3kw, automatic transfer switch goes to input 2 which is fronius pv point.

Does it make sense?


Fronius
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Fuchs avatar image Matthias Fuchs commented ·
I have a similar setup:

* Fronius Symo Gen24

* Multiplus II 48/3000 connected to Phase 1 on AC-IN + Pylontech battery

If the grid goes out, the symo supplies the PV point plug. The multiplus supplies power through the battery to AC-OUT.

My question is, can I connect the PV point to the AC-OUT port.

Anything connected to AC-OUT would now take power either from the Symo PV-Point OR if not available, from the battery. If there is no consumption, the multiplus would load the battery, if needed.


Is this setup possible?


0 Likes 0 ·
2 Answers
sharpener avatar image
sharpener answered ·

<If I understand what you say correctly...>

Obviously I did not!

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Robert Boerescu avatar image Robert Boerescu commented ·
Fronius symo gen 24 is a three phase inverter and it is on ac in connected to the grid. Easysolar 2 is only connected to one phase and it is working for critical loads with ac out.

pv point is a fronius basic backup solution which gives up to 3kw on on separate output line, single phase if the grid goes out and there is sun. If a battery is connected to the gen 24 than it can use the battery also. I do not have a battery for fronius because it supports only high voltage byd at this time and they are expensive. Fronius also has a 90 seconds blackout even for their full backup solution so you cannot really use it for critical loads if you do not want them to stop. This is why I have the victron also.

pv point comes up as I said if the grid goes out and in theory I would not need it because I have the victron. However if the blackout goes for a longer time and I run out of battery I was thinking that I could use pvpoint as an alternative ac in using a transfer switch.


0 Likes 0 ·
Show more comments
bulraydin avatar image
bulraydin answered ·

Hi @Robert Boerescu


I am thinking of doing the same setup. Have you been successfull in the mean time ?


The difficulty in connecting a PV point to the input of a multiplus is , that you never know how much power is available at the PV point. Hence maybe it is like a weak generator connected. I will try some scenarios. I will first try the dynamic current limiting. I guess this is the right feature which will draw current from the source as long as the source allows it.


Let me know your comments and experiences


Best regards

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Duivert NL avatar image Duivert NL commented ·

you can add a meter to your setup and configure it for PV on ac in

see for compatible meters:

https://www.victronenergy.com/upload/documents/Datasheet-Energy-Meters-Selection-Guide-EN.pdf