Speccing out a home battery storage system using a multiplus II 48/5000 230v. Looking at the maximum AC in - this is rated at 50amps (11500va), so could be run in 10mm2 cabling, however if I've understood correctly the AC out side with powerassist could potentially deliver the grid feed in of 11500va plus a further 5000va from the inverter. So at 16500va (or 16.5kW) you would need 16mm2 cabling to feed back to the load side (consumer unit) - using online cable size calculator. Looking at the spec sheet the inverter only has 13mm2 terminals? So here in the UK, it's either 10mm or 16mm. 10mm is under-specced and 16mm won't fit in the inverters terminals. What am I missing?