6 Modules serial with 250 or parallel 3x2 with 150 ?

Hi,

i would like to to wire 12 identical Axitec 415wp (Axipremium XXL HC BLK) modules -> RS450 does not fit very good based on the excel calculator, so i have to go for smartsolar. No shadow, all 12 modules pure perfect sun in perfect orientation.


Doable is 1x6 (250/60) orr 2x3 (150/60)

2x 150/60 is around 300Euro cheaper than 2x 250/60.

System is 48V and another large AC inverter exist as well with 3 Multiplus.
Is there any disadvantage going with 2x 150/60 ?

Not sure - Admin please assign or create
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
bunya-solar-pl avatar image
bunya-solar-pl answered ·

I can't see any disadvantage in going with 2 of the 150/60 regs except for larger cable size on the solar side of the reg as will be twice the current as the 250/60 situation. You'll also need some way of paralleling the two strings of 3 panels together. If they have MC4 connectors you can use MC4 parallel plugs.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ahtrimble avatar image
ahtrimble answered ·

I looked up your PV...38v/14a if I read it right.

If you go with 4 strings of 3 panels that gives you 114v / 56a total. That is kinda cutting it close when you are talking ideal conditions and you might exceed the 150/60.

I have the MPPT 150/70 which would give you a nice safety margin/cushion. So you might want to consider the 150/70. And I use 2AWG from MPPT to batteries, fuse and switch.

Something to think about.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

grobalt avatar image grobalt commented ·

Thanks for your reply, you would add 12 modules to one MPPT ?

The "issue" with 3 parallel is i have just one cable (6mm, about AWG 9.5) and i cannot add more without creating a huge construction site -> and 3 parallel is up to 40A -> MC4 connector on the roof are just certified up to 30A.


4s3p is exceeding the 150V by far

1669620682104.png

2 AWG -> i will use 35mm as the maximum is for the MPPT.


250/85 as the online MPPT calculator proposes:

1669620771524.png

I don't understand why is the website not proposing 250/100 (100 Euro/USD more than 250/85)? Because even that model is limiting / saturating in power (A) ?

1669620849979.png

as we have with the 250V room for higher voltage -> 6p2

1669620944753.png


1669620975581.png


Finally a 3 by 4

1669621225725.png

1669621251154.png


If i am not completly wrong, the modules will be most of the time between 10 and 45 C° -> so capped .


Module looks like:

1669621490914.png

If i follow the Victron MPPT webseite is recommends 85. 85A / 12 Modules is 7,08A per Module which means the MPPT is capped when ~ 500W/m² irridiation, correct ?

0 Likes 0 ·
1669620682104.png (156.5 KiB)
1669620771524.png (155.9 KiB)
1669620849979.png (150.6 KiB)
1669620944753.png (209.8 KiB)
1669620975581.png (151.0 KiB)
1669621225725.png (200.4 KiB)
1669621251154.png (149.9 KiB)
1669621490914.png (184.4 KiB)

Related Resources

Additional resources still need to be added for this topic