AC input connection delay when using a generator

Hi.

Is there any good way to delay the connetion of a generator to a Multiplus, so that it can warm up for 5 minutes before the AC input connects and start loading the generator?

Generatorgenerator auto start
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Jason - UK avatar image
Jason - UK answered ·

@Kjellare Yes, you could use an assistant for that. You can use the AC input Current Control assistant and a temperature sensor connected to the generator.

1669196893503.png


1669196893503.png (171.8 KiB)
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cgesmike avatar image cgesmike commented ·
In a situation where it isn't realistic to use a temp sensor on the genset - and ags is not use - is there a simple way to change the delay time? Currently, my MP-II automatically delays 15 seconds from the time it senses voltage at the input to the time it begins to use that generator power. It would be great to just be able to adjust that 15 seconds up to a longer period.