I have a 3 phase Victron system (3 x Quottro 8kVa), with a Freedom Won 30kWh battery
I have integrated a 30kVa 3 phase generator (Generator on AC Input 1 and Grid on AC Input 2)
When Grid is lost and battery goes down to 40%, the generator starts automatically, but it is not being accepted by the inverters, and it keeps on trying, but fails, probably because of high loads
I have made a test, and with all other loads off, the generator kicks in, but only ONE inverter charges the battery, at 3000 watts, the other 2 inverterss only kick on briefly, for just about 10 seconds, then they stop charging
The generator is 30 kVa , so it has 10kVa per phase
On VE configure, AC 1 Input current limit is 35 amps (for generator)
On the "Charger" tab, max charge current is 60 amps
Are there any changes that need to be made?