Hi There,
If I have a Cerbo on the LAN as the Fronius units, do I need to load the PV Inverter Support assistant when AC coupling with Fronius Inverters?
I would expect that I still need the frequency shifting as backup?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi There,
If I have a Cerbo on the LAN as the Fronius units, do I need to load the PV Inverter Support assistant when AC coupling with Fronius Inverters?
I would expect that I still need the frequency shifting as backup?
Pv inverter support is for offgrid setup.
If you are on grid or mostly connected, use ESS assistant.
Victron with AC PV online training
AC-coupling and the Factor 1.0 rule
AC-coupled PV with Fronius PV Inverters
Connecting a PV Inverter section of GX manual
AC-coupled PV with Fronius PV Inverters live docs
Fronius Webinar: Fronius & Victron Energy: Easy system set-up
Fronius Advanced Webinar: AC Coupling with Fronius & Victron (AFR)
Fronius Webinar: Smart rural electrification with Fronius and Victron Energy
34 People are following this question.