Hi.
System is quattro with fronius on the ac out with 9kw of panels and byd 13kw batteries. Ccgx is showing charge current limit of 30amps and sending loads to grid.. battery is at 45%.
How do i adjust this please
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi.
System is quattro with fronius on the ac out with 9kw of panels and byd 13kw batteries. Ccgx is showing charge current limit of 30amps and sending loads to grid.. battery is at 45%.
How do i adjust this please
OK, so i've worked it out!! the battery was cold abd the byd was reporting max current it would accept, need to keep it warm!!
Please see this discussion - https://community.victronenergy.com/questions/1155/byd-dvcc-cold-weather-performance.html
Low charge current limits are most often due to cold battery temperatures. There are limited options beyond warming the batteries.