MPPT Lightning?

a1639cbb-ba63-4250-8fec-c7dd4ec80f3a.jpegWas it a lightning strike? The line is good on top the roof and none of the panels appear to be damaged. It says it’s still charging the batteries, should I let it continue until I can get it replaced, or should I disconnect it immediately?

MPPT Controllers
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
It is a good thing concrete blocks dont burn.
0 Likes 0 ·
Trevor Bird avatar image Trevor Bird commented ·

Looks like a simple case of a bad connector. Its not lightning, just a high resistance joint in the connector. Things fail sometimes.

0 Likes 0 ·
2 Answers
Alexandra avatar image
Alexandra answered ·

@joshuagoshert

Fire (almost) usually because cable/connector has become hot causes the soot like that.

There are two reasons for hot cable: -

1. Undersized cable (or incorrect cable) for the amps.

2. Bad connection (either a bad crimp, poor/bad matching connector, or connector not home correctly)

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

joshuagoshert avatar image joshuagoshert commented ·
Ok, but it’s been the same configuration for 4 years, with professional installation. Any ideas what might cause the overload of amps if not lightning?
0 Likes 0 ·
Show more comments
anthony avatar image
anthony answered ·

Badly crimped MC4 or poor quality MC4 connector resulting in inadequate contact area between mating faces which manifested over time. If you have historic data recorded on the system you may see output getting progressively worst.

There should not be two conductors going into one MC4 connector as there appears to be. The solar input cable appears to be of very small cross section area and does not look like solar cable.

No strain relief on cable evident.

It would be useful to know the quantity and output of panels, battery voltage and complete model of MPPT in original post.

You should disconnect if you haven't already.