Multi 24/3000 Bulk and Absorption lights constantly blink. Not Trying Equalization

Victron Nube here, familiar with OTG and Inverters.
As the title states my Bulk and Absorption are constantly blinking yellow. In the manual it is stated that this is

"The mains voltage is switched through and the charger operates in equalize mode."

I have not requested an Equalize charge, I turned off that function via software.

Has anyone seen this ?


Links to Photos of System with Video - Click here for Google Gallery

I have pasted my config file below >


TAB: General
System frequency    60Hz
Shore current    8.0    A
Overruled by remote    checked
Dynamic current limiter    unchecked
State of charge when Bulk finished    95.0    %
Battery capacity    230    Ah
Charge efficiency    0.95    
TAB: Grid
Country / grid code standard    None:               (feeding energy from DC to grid not allowed)
Accept wide input frequency range (45-65 Hz)    checked
AC low switch mains off    94    V
AC low switch mains on    101    V
AC high switch mains on    138    V
AC high switch mains off    143    V
UPS function    checked
TAB: Inverter
PowerAssist    checked
Assist current boost factor    2.0    
Inverter output voltage    120    V
Ground relay    checked
Inverter DC shut-down voltage    18.60    V
Inverter DC restart voltage    21.80    V
Low DC alarm level    21.80    V
enable AES    unchecked
TAB: Charger
Enable charger    checked
Weak AC input    unchecked
Stop after excessive bulk    unchecked
Lithium batteries    unchecked
Storage mode    unchecked
Use equalization (tubular plate traction battery curve)    unchecked
Charge curve    Fixed
Absorption voltage    24.40    V
Float voltage    24.40    V
Charge current    8    A
Repeated absorption time    1.00    Hr
Repeated absorption interval    7.00    Days
Absorption time    1    Hr
TAB: Virtual switch
TAB: Usage
Virtual switch usage    Do not use VS
TAB: Assistants
TAB: Assistant Configuration
Assistants not used



Multiplus-IIbattery chargingled
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Paul B avatar image
Paul B answered ·

Hi troy

I have looked up the Victron tool kit app and It shows that the issue is Voltage sense error

Also I would sugest that you install the latest firmware as well

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tr0y avatar image tr0y commented ·

Thank you !

0 Likes 0 ·
boekel avatar image
boekel answered ·

It's measuring 0v DC, but still inverting. check wiring (voltage sense input used for something else?) and as Paul says: update to latest firmware if not yet done.



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tr0y avatar image tr0y commented ·

Thank You !

0 Likes 0 ·
tr0y avatar image
tr0y answered ·

After speaking with my reseller support, it is my understanding that the voltage sense cable that Victron shows in the documentation, doesn't actually exist for sale and I should make one from 18g speaker wire, somewhat unimpressed. I am waiting on correct wire ends / terminators to do so and will report findings back. Beginning to feel nickel and dimed to death. Really want to like this product...

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

The unit should work just fine without the sense-wire, but somehow it doesn't so my thought was there might be something else connected to the sense-input. (like the temperature sensor)

Do you have pictures of the install / wiring?

0 Likes 0 ·