If that Temp Comp figure is in play the setpoints get changed. That won't show in the settings, but the real V it's targeting will alter.
Before trying to answer, please give us more information. You have 24V batteries?
System is configured for 36V, but voltages are set too low for that?
Running 24V batteries at 36V will kill them very quickly and will lead to poisonous gas being emitted.
I’m running a 8S prismatic cell configuration.
You have set you battery voltage in the mppt as as 36v?
And a bulk / absorption as 32.57v?
Yet your float voltage is higher at 32.73v?
And you have 24v system components?
You need to check your battery and system parameters again.
Those are test values for the purpose of this problem of overcharging that I’m having. Normally I run closer to 33V, as it is a 8S lithium Ion cell configuration.