Generator input on 3 parallel quattro's single phase

Hi, I have 3 quattro's in single phase giving 45kw. I want to connect a generator of about 8kw. Can i connect it to AC in 2 on just one quattro or does it need to be accross all three equally? If so can i turn the power down enough so i don't trip the genny


thanks


Dave


Generator
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image derrick thomas commented ·
you would need to connect the generator input to all 3 units using same size and length of cabling. If you have a gx device you can set the input current limit desired for the generator and the gx device will do the math between the quartos. With no gx device you will need to set the current limit individually in each quattro. Each quattro will need to be set to 1/3 of the desired input current limit.
1 Like 1 ·
Show more comments
1 Answer
Paul B avatar image
Paul B answered ·

yes you can turn the ac power in limit down if you cant get it low enough then turn off power assist in all 3 inverters using ve Bus system configure. This will then allow you to lower the ac in amps further.