Custom NMC 14S 48V bank.
Successfully configured WM5 to control system for a few months. Relatively happy with it.
Issue is with cold temp charging. Obviously, I want to restrict charging to 0A below freezing. To give myself some margin, I have specified 5°C as a limit, i.e., if below 5°C, charge is not permitted.
When below 5°C, the MPPT 250/100 will power loads, but "charge" is throttled to between 0.2 and .05A (starts at 0.2A and increases to 0.5A as temperature approaches 5°C).
The Batrium Shunt and my BMV-702 report identical values.
Consistent with their poor support as of late, Batrium says, "not our problem, contact Victron."
It's my understanding that when my MPPT says "External control" it's ONLY doing what the BMS is telling it to do, so if it's sending 0.2-0.5A to the battery, this is a result of whatever criteria the BMS is feeding it.
Any ideas?