BMV-712 Smart Initial Capacity Setting

On initial setup I have to enter amp capacity of the batteries. Am I entering the total amps of the batteries or 50% of the total that I can use. I have flooded batteries.

monitoring
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Enter the total Amp-hour capacity of the battery bank.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

But you can set the 'discharge floor' to 50% - that way the time to go calculation will consider this level of discharge in the 'time to go' calculation.