question

Tom Ranson avatar image
Tom Ranson asked

ESS going into Sustain too soon

Hi all,

Grid parallel ESS

Cerbo GX with ESS with DVCC

MultiPlus ii

SmartShunt

2x MPPT 100/30

24V battery bank (8x 6V FLA in series/parallel)


My ESS is going into Sustain far too early, when the batteries are only at c. 90% SoC. I have it configured as Optimised with Battery Life.

I believe that the reason for this is the values configured for the Dynamic Cut Off, however I am using the ESS default values for Gel/AGM batteries, as I believe this is the closest battery type to my FLA. I am seeing the system enter sustain mode at 23.99V, and therefore my batteries are not discharging significantly (minimum SoC set to 50%). I believe I should be able to take the batteries down to 23.00V without any issue or risk of damage.

Could anyone guide me further on this or help me optimise my settings please? I'm not sure that my dynamic cut off values are appropriate for FLA batteries, but can't find any documentation or guidance on this anywhere.

ESSbattery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
gfillary avatar image
gfillary answered ·

Im having the same issue. I'm running a 48v system with a multiplus II with 8 x 170Ah power safe batteries after starting with 100% fully charged, it goes into idle mode after on 4.5Kwh has been drawn. However my smart shunt is still saying I have 50.20v's

Im missing as setting somewhere....

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image
nickdb answered ·

People, SOC is a derived metric. If the measuring instrument is flawed or setup incorrectly then it is meaningless. Voltage is king. You can only hit sustain if you have setup ESS wrong or the voltage dropped long enough. Read the manuals, setup your systems properly and it will all work out. These are bleak posts that just suggest you need a professional to help.

19 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
Hi @Alexandra thank you. Yes, I have read and re-read the documentation and still can't fathom what the correct and safe dynamic cut-off values would be in my situation with FLA batteries. There is no help in the documentation for this battery scenario, and as far as I can tell, no useful information on the forums.


If you could assist me with understand what would be appropriate values in my specific use case, I would much appreciate it please.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·

@Tom Ranson

It is hard to say, as they are also affected by age, bank size, battery manufacturer recommendations.

For the most part as long as they are not below your low DC cut off, you will be fine. Even setting them all the same to eliminate that setting as the problem.

You can still program your inverterter to shut off at a certain SOC (depends on how you want to use them). FLA does have quite a voltage collapse under higher load.

All I can say is you need to experiment. Use the VRM or GX to see where the voltage drops under each c rating load and set it from there.

The discharge curve graph information from the battery manufacturer will help as well as it usually shows how the battery acts or is supposed to act under different loads.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Alexandra ♦ commented ·

Most batteries do not have a default setting on the Victron by the way, so you are not in your own boat there.

Are you running your batteries as a keep charged system?

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·

Hi @Alexandra as optimised with battery life. The problem is that Leoch don't seem to publish much useful information for my DT126 batteries. I believe they are essentially a Trojan T-105 knock-off though.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
Hi @Alexandra

So my low DC cutoff (for sustain) is currently 23.00V. This I understand is a safe lower voltage and represents 50% SoC as far as battery voltage goes for these batteries. I do not wish to discharge my FLA's below 50% DoD.

My MPii inverter is also configured to shut off at 50% SoC, however at the moment we're not getting anywhere near that before it goes into Sustain, due to hitting the dynamic cut offs.

So are you saying that it might be appropriate for me to set all four dynamic cut off values to 23.00V?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·

@Tom Ranson

Yes that is what I am saying to do.

We are now troubleshooting and then we can work out frommthere what to do.

See how the system runs at each c discharge after that and if sustain is triggered again.

What size multiplus do you have? Is it the 3kva?

Looking at the discharge curve 6v per cell at 75A is where it is rated new.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
@Alexandra ok, I will set all 4 to 23.00V for testing and monitor it. I don't see how any harm can come from this as if anything the inverter will still go into sustain too early due to the voltage collapse at higher currents.


Sorry for being thick, but how should I go about testing how it performs for each c discharge? I am by no means an expert and am trying to learn more every day.


Yes it is the 3kva MPii.

0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Tom Ranson commented ·

@Alexandra actually, here are the default values for the Gel/AGM battery type. So setting them all to 23.00V would not be appropriate I don't think? I look forward to your advice.screenshot-2022-10-23-123233.jpg

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ Tom Ranson commented ·

What size inverter do you have?

And what load is on the system when sustain is triggered.

Bow often does the system get to a full charge (by definition this is all the way through a full absorption)


0 Likes 0 ·
Tom Ranson avatar image Tom Ranson Alexandra ♦ commented ·
  • @Alexandra It's a 3kva inverter, however it's currently significant limited to only 250W (another problem, another story which I am discussing with Victron).


The load last night when it hit sustain was only 250W, so approximately 10A.

The batteries get a full charge every night on an ESS scheduled charge (cheap rate electricity).

0 Likes 0 ·
Show more comments
Tom Ranson avatar image Tom Ranson commented ·
Hi @nickdb thank you for your response. I totally agree and understand that SoC is only a calculated metric, however I am still struggling to know what is the best practice for the dynamic cut off values when using FLA batteries (as there is no corresponding battery type default in ESS), which isn't documented or as far as I can find, discussed on these forums.
0 Likes 0 ·
hereandthere avatar image
hereandthere answered ·

@Tom Ranson I'm experiencing similar issues. My system is with 4 200Ah lead-carbon batteries in series on a easy solar gx with smart shunt.

Did you find the right settings for your system to work properly?

Is it really that simple to just alter the cut-off settings?


O and one more thing, I'm trying to do a full charge every day (when the price is low) but set the ess at green doesn't charge to 100% for some reason I can't figure out.

A pink bar (grid to battery) does appear, and as the time passes the pink bar moves in time and keeps moving up to the evening when the price is high again without any charging. And; there is this yellow notification on the dashboard: "battery balancing is scheduled for today" but it doesn't?! I am confused


Any tips would be appreciated


H


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

What is ESS training video

ESS Quick Installation Guide

ESS design and installation manual

Additional resources still need to be added for this topic