Hi,
I would appreciate your comments on using MPPTs in east-west roof orientation.
I have a roof that has west(-70dgr) / east (+110dgr) position and I intend to place 16 panels on each side. The idea is to connect them in four 4S1P loops on each side. My original idea was to couple 2 loops to a 250/85 MPPT ie 4 loops to 2 MPPTs on each side.
What I'm wondering is how good it will be if I connect all 8 loops to 2 larger MPPTs (250/100) in such a way that two loops from the WEST and two loops from the EAST go to one MPPT.
The voltage should be OK, because the four loops are connected in parallel. Max current can be a bit debatable but from what I know due to the position of the panels they will never produce the same amount of energy at the same time. My calculations show that the maximum current for two loops is approx. 75A at an extreme temperature of -20C and at 12-2pm in SOUTH position!
I think my panels in west-east orientation will never produce more than 60-65A as a max probably less and when one side is at its max, the other is at its minimum or very little. Therefore, I think it could work with two MPPTs without cut-offs. What do you think?