Hello,
Our installer just installed a Victron Phoenix Smart 50 amp 3 bank charger to new 2 lithium battery banks (4 total). We didn’t know what to do about the float setting, as Victron’s website suggested 13.2V however the manufacturer's website said that a constant float charge will degrade the battery. See excerpts below.
Can the float setting be zero? What happens if I’m not on the boat for an extended period, but it’s connected to shore power?
Thank you for any help you can offer.
From Victron:
6.4. Lithium batteries
Lithium Iron Phosphate (LiFePo4) batteries do not need to be fully charged to prevent premature failure. The default lithium (and recommended) settings are:
Setting |
12V system |
24V system |
48V system |
---|---|---|---|
Absorption voltage |
14.2V |
28.4V |
56.8V |
Absorption time |
2h |
2h |
2h |
Float voltage |
13.2V |
26.4V |
52.8V |
From the manufacturer:
Should I use float chargers or battery maintainers for my lithium battery?
No, LiFePO4 batteries should be disconnected from the charger when fully charged. Float charging, or maintainers are not good for lithium batteries. Keeping a constant float charge or topping off charge also can cause metal plating and will reduce the lifespan of lithium batteries. Dakota Lithium batteries also have a low self-discharge rate of <5% a month. This low self-discharge rate makes a battery maintainer for long term storage un-necessary (for more on battery storage see section below).