question

jpcirig avatar image
jpcirig asked

float - Lithium manufacturer says no?

Hello,

Our installer just installed a Victron Phoenix Smart 50 amp 3 bank charger to new 2 lithium battery banks (4 total). We didn’t know what to do about the float setting, as Victron’s website suggested 13.2V however the manufacturer's website said that a constant float charge will degrade the battery. See excerpts below.

Can the float setting be zero? What happens if I’m not on the boat for an extended period, but it’s connected to shore power?

Thank you for any help you can offer.



From Victron:

6.4. Lithium batteries

Lithium Iron Phosphate (LiFePo4) batteries do not need to be fully charged to prevent premature failure. The default lithium (and recommended) settings are:

Setting

12V system

24V system

48V system

Absorption voltage

14.2V

28.4V

56.8V

Absorption time

2h

2h

2h

Float voltage

13.2V

26.4V

52.8V



From the manufacturer:


Should I use float chargers or battery maintainers for my lithium battery?

No, LiFePO4 batteries should be disconnected from the charger when fully charged. Float charging, or maintainers are not good for lithium batteries. Keeping a constant float charge or topping off charge also can cause metal plating and will reduce the lifespan of lithium batteries. Dakota Lithium batteries also have a low self-discharge rate of <5% a month. This low self-discharge rate makes a battery maintainer for long term storage un-necessary (for more on battery storage see section below).

float
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @jpcirig

For lithium batteries you should see the 'float' stage as a 'not discharging' stage:

An lfp battery has a resting voltage of about 13.2-13.4 volt, by setting 'float' voltage to that level, if there is power use (for example in a boat or RV: lights, DC equipment, alarm), this power will come from the charger (if the load is not bigger than the charger can supply)

So: the battery is not really charging in the 'float' stage and won't damage the batteries.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image
klim8skeptic answered ·

Dakota Lithium sell and recommend Victron SmartSolar mppt's.

Either the Lithium battery preset in the mppt is ok, or perhaps DL could be contacted for the recommended settings.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@jpcirig

You have a few options.

One is to set reabsorption more often so the battery moves up and down between float (the rebulk offset lower) and absorption voltages.

The victron chargers dont really keep the system at kne voltage continuously unless they are in use or under load.

Or for longer periods to shutdown and disconnect the system.

But in any case the battery manufacturer needs to be contacted for clarification as klim8skeptic mentioned.

Float chargers are different though they may be referring to non intelligent older ones that are always on and trickling low amps into the battery? Again clarification may be needed there.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jpcirig avatar image
jpcirig answered ·

Wow - thank you for the fast and thorough replies. My experience with DL was not so good. They seemed to be resellers of batteries and directed technical questions to "a local marine electrician". The few marine electricians I've spoken with all responded with, "you shoulda used Brand X" and "just switch back to lead-acid". So, I'm stuck with $5k "drop-in lead acid replacement batteries" and little support on how to make them work. So again - thank you for your help!

With that said, I did find the following excerpt from the Phoenix manual. It indicated that when Li-ion mode is selected, the float feature is disabled. However, the Storage Mode is enabled at 13.5V. I couldn't find an explanation of storage mode vs float mode. Any thoughts?


From Phoenix manual:

6.1.1 Charge Voltage

By simply selecting the integrated charge mode appropriate for the battery type being charged, (refer to the battery manufacturer’s recommendations) the voltage settings for each charge stage will be altered according to the table below:

Mode

Absorption

Float

Storage

Recondition

12V

24V

12V

24V

12V

24V

12V

24V

Normal

14.4V

28.8V

13.8V

27.6V

13.2V

26.4V

Disabled

Normal + Recondition

14.4V

28.8V

13.8V

27.6V

13.2V

26.4V

16.2V

32.4V

High

14.7V

29.4V

13.8V

27.6V

13.2V

26.4V

Disabled

High + Recondition

14.7V

29.4V

13.8V

27.6V

13.2V

26.4V

16.5V

33.0V

Li-ion

14.2V

28.4V

Disabled

13.5V

27.0V

Disabled

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
It is probably best to describe how you are intending to use your batteries,


and how you are intending to recharge them.
0 Likes 0 ·

Related Resources