3-phase ESS unnecessarily feeds the grid when phase loads unbalanced

My ESS system starts feeding the grid from the battery when I put a high load on one of the 3 phases, while the other two phases are almost not loaded. This seems to be a reoccurring problem after a few tests.

Phase compestation is set to "total of all phases". The grid setpoint is set as +10w.

When all 3 phases are sort-of equally loaded, high or low load, this does not happen.

Any ideas what is going on here?

ESS with 3x multi 3K, AC coupled with 10kw Fronius symo (on AC-in, vrm dashboard incorrect due to using external current transformers) , 8x pylontech US2000C

The multi's use 3 external current sensors which are correctly installed with the 5 meter wires.

EDIT: this seems to only happen when the total load is higher than the PV output, and when above 24A (+-5,5kW load on one phase)

img-5555.pngscreenshot-2022-10-19-at-124213.pngscreenshot-2022-10-19-at-124151.png


ESSess discharging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
marekp avatar image
marekp answered ·

@MichaelVH

Try setting "individual phase" but sudden changes in load result in short power imbalance.

BTW.

You cannot have 10kW Fronius on the AC-out of 3xMP/3k.

21 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michaelvh avatar image michaelvh commented ·

It seems like it is not a short power imbalance, but sustained once going over 24A on one phase.

No worries, the AC inverter and all loads are on AC-in, the VRM dashboard shows it on AC-out because we are using external current transformers for measurement

0 Likes 0 ·
Show more comments
michaelvh avatar image
michaelvh answered ·

Confirming that it is not a calculation issue on the VRM side, the utility grid meter picked up the same unwanted injection at the time of very unbalanced load on one phase. If anyone could reproduce this, or has an idea why this happens, i would be glad to hear.

Remark: injection is allowed here, it just doesn't make sense to do so while draining the batteries.

screenshot-2022-10-20-at-140651.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

maha avatar image
maha answered ·

I think it's the same problem like here:3,5mm Sensorbuchse

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michaelvh avatar image
michaelvh answered ·

So i finally found out why… the system was configured in ve-confugure with a 16 amp breaker on ac-in. The system is trying to keep L2 under 16A by feeding some extra juice to the grid on this phase. The phase feeds are asymmetrical.

note to Victron team, in these cases it would be possible to feed less to the other phases? To keep the total output zero?

2 |3000