I have a system with 2 x 10kva quattro's in parallel and 60kWh battery and about 20kW solar pannels with 2 x smartsolar 250/100 and 1 x smartsolar rs 450/200.
Imgettinglow battery alarms on different soc. Sometimes 40% sometimes 20%. The battery voltage is stillabove the low battery alarm setting. If there is no grid the system shuts down above 52v even though shut down voltage is 47v.
The alarm comes every view seconds so its a lot of alarms.
Today the battery voltage went down to 51.5v at 20%SOC no alarm when the battery started charging the errors started at 52.2v.
Checked all connections, battery coms is fine.
See all settings below.
DC Low Shutdown 47v
DCInputlow restart 51v
DC Low pre alarm 50v
SOC Low shutdown 10%
SOC low Restart 20%
Charging voltage 55.8v
ESS Settings
Sustain Voltage50v
Dynamic cutoff
0.005c 48v
0.25c 47.8v
0.7c 47.2v
2c 46.8v
All settings supplied by battery manufacturer.