Hello.
Does anyone have experience or knowledge of how to set the maximum charging in DVCC if I have feed to grid enabled? If I have it disabled, setting the maximum charging current DVCC works, but if I enable the feed, it ignores any settings and is able to push 100-150A into the battery. I received information from the distributor that this is not possible, but nowadays, when virtual battery services are provided, it would be nice if charging could be controlled.
Example:
Production 4000W
Household consumption 500W
Battery charging 100W
The rest to GRID 2500W
Is something like this possible?

When Feed to GRID is DISABLE , everything work. But when I enable Fee to GRID and battery is not 100% , all energy what I generating push to battery . Why ignore DVCC setting ? If I enable Feed In and I generate much energy than DVCC - max charging limit is , excess generated energy let it flow to GRID.