The Multi RS Solar uses about 250W with AC1-IN connected, is there a setting that will only connect AC1-IN if battery voltage goes low?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Abend lintech,
wie hast du das genau herausgemessen?
viele Grüße Dan
Danke schoen.
In another discussion thread, you showed a picture of a meter indicating 1.36 Amps.
In Alternating Current circuits, 1.36 Amps does not always correspond to 312.8W. It could correspond to only 25W. This is because AC circuits also carry Reactive Power back-and-forth between supply and consumer. So if you measre 230V and 1.36 A, the most you can say is that you measured an APPARENT power of 312.8 VA (Volt-Ampere). But you don't know how much of it is active power (Watt) and how much is reactive power (measured in VAR). The ratio of active to apparent power (W / VA) is called the power factor and is a characteristic of the load. Residential customers are billed only for the active energy used. Industrial customers are typically penalised for low power factor.
Grid-connected inverters use reactive power to detect if they are connected to the grid. It's part of the active anti-islanding protection required by IEC 62116:2014. The following is a quote from the documentation of another inverter:
The reactive current component injected by the inverter changes periodically (a reactive current pattern cap. and ind. with no reactive power on average). The reaction of the frequency on this reactive current pattern is measured and analyzed. In case of grid connection the grid frequency will not be influenced by the change in reactive current. In case of an island operation the reactive current pattern causes a change in frequency. The analysis of the measured frequency pattern clearly indicates the island and the inverter trips.
@MondeoMan Hmmm, after reading your comment I went back to the external meter and checked the values and was surprised to find the values as what would be expected. Watts were 5.6W, Amps 1.16A and PF at 1.00. I now understand where I got the values from. The 250W value was viewed from a completely different metering setup which still shows 250W even though the external meter is showing 5.6W. Had I looked at the watts on the external meter I would have noticed it was 5.6W and that the other metering setup shows 250W. This must be its lowest value displayed on any value above zero and below 250W. A classic example of making assumptions based on incorrect data, I concede, my error.