Hi,


I’m going to have a Victron instalation from local company. It contains:

- 3x Multiplus II 48/3000

- MPPT SmartSolar 150/100-Tr

- 12x 450Wp panels

- 3x Pylontech US3000C

- GX monitoring


I have bought additional 8x 260Wp panels from a friend for a very good price and want to add them to the system. The company doesn’t want to do that by themselves, so I have to do it by myself. I’ve calculated MPPT from the Victron calculator and here are some questions:

- is it a problem that the two mppts are not the same size?

- will I see both in the VRM portal? I read that if I connect them via VE.Direct, it would be possible. Is that correct?

- just to be sure, with multiple mppts, I also need the SmartShunt

- anything else I need to be aware?


Thanks a lot

MPPT Controllers
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

- MPPT SmartSolar 150/100-Tr

- 12x 450Wp panels

I would be asking for details about the suitability of a 150-100 being connected to 12 x 450w panels.

Victron online MPPT calculator.


0 Likes 0 ·
Show more comments
1 Answer
klim8skeptic avatar image
klim8skeptic answered ·

- is it a problem that the two mppts are not the same size?

No. Just make sure you have pv strings that voltages/currents that are within the mppt's pv input specs.

- will I see both in the VRM portal? I read that if I connect them via VE.Direct, it would be possible. Is that correct?

Yes

- just to be sure, with multiple mppts, I also need the SmartShunt

NO, the BMS will pass voltage/current/SOC onto the GX.

- anything else I need to be aware?

Read the .Pylontech Product & system compatibility page.

Esp the "2. Minimum Battery Sizing Recommendations".

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jakudo avatar image jakudo commented ·
Hello,


thanks a lot for the answers. Ok, I will check the battery sizing.


Jakub

0 Likes 0 ·
sharpener avatar image sharpener jakudo commented ·

With 6 parallel strings you have potentially got >60A in 6mm^2 cable and a voltage drop of 4V which is double the 3% allowed. Get them to increase the cable to 10mm^2.