450/100 vs 250/100 - bad Performance

Hi everybody!

I have one Array (At the moment) containing 8 panels with total 320 Voc.

First I had the 250/100 installed with 2x4 panels and the yeild was good.
Now after switching to the 450/100 rs and the change to one string in series I have the feeling that I am missing 15 to 20 % of my yields. Of course winter is aproaching but over the last year I got quite a good feel for my 250/100 chargecontrollers, and something is off. Its always 1 or 2 kwh less than it used to be with the 250/100.

Why is the performance of the 450/100 rs worse?
Already did an update and .. well nothing changed.

Sincerrely
Adam J.


MPPT Controllersmppt rs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Individual trackers are limited to 4000W (18A PV side)

Spread the panels across both.

All documented in the spec sheet.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

testor90 avatar image testor90 commented ·
Thank you very much but 4000w were never reached in this confiuguration, even with the 250/100 because of the orientation (flat, no shadows)


So this was not the limiting factor.