VRM: How to get rid of "AC Loads" on input?

Hi All

My VRM is showing an "AC Loads" on the input to my Quattro.

What is this?

1664698720891.png

The Touch GX / remote console show the smae thing:

1664699073693.png


There is an ET112 on the grid connection, but there are no loads connected between the grid connection and the Quattro.

I'm guessing this is some kind of calculated value based on what the Quattro thinks the input is, and the value measured by the ET112 - is that right?

Is it possible to remove this "AC Loads" from the displays?

In addition, is it possible to rename the other tiles?

Many thanks

Kind regards

John

cerbo gxVRM
1664698720891.png (54.2 KiB)
1664699073693.png (36.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

8 Answers
nickdb avatar image
nickdb answered ·

Under ESS settings, disable show Inverter show AC loads.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnparvic avatar image
johnparvic answered ·

Hi Nick

Under ESS I see:

1664702583849.png

1664702609941.png


This is on 2.91 Large

Any further pointer as to where to find this option?

Many thanks

Kind regards

John



1664702583849.png (25.6 KiB)
1664702609941.png (20.7 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Disable inverter AC output in use.
0 Likes 0 ·
johnparvic avatar image
johnparvic answered ·

Thanks Nick... but...

Nope - that turns off display of the inverter outputs!
1664703681596.png

The "AC Loads" on the input side is still showing!

Any other ideas?

I don't see this tile on other peoples posts of their systems.

Kind regards

John


1664703681596.png (25.4 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
hmm. Under settings energy meters, what role have you selected for the meter?
0 Likes 0 ·
johnparvic avatar image
johnparvic answered ·

Hi Nick

"Grid meter"

Kind regards

John

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnparvic avatar image
johnparvic answered ·

This problem still persists.

Why is my system showing "AC Loads" on the Quattro input?

Thanks

Kind regards

John

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@johnparVIC

You see the "AC loads" on the inverter input because you have external power meter on the grid input. The "Ac loads" value is calculated.

If one uses inverter to measure grid values, the "AC loads" is not shown.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

n-dee avatar image
n-dee answered ·

Hi,

In ESS i switched Grid Metering from External meter to Multiplus. (Quattro in your case)
This may be done if the whole house is connected to the Multiplusses/Quattros and disables the normal loads

br,
Andy

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnparvic avatar image
johnparvic answered ·

Thanks both

So, my guess was right, it's the difference between the ET112 and the Quattro's idea of what the grid connection is doing.

In my case, that is not interesting at the moment as I don't have any actual AC Loads on the input side.

It would be great if it was possible to simply disable showing the "AC Loads" tile. Does anyone know if this would be possible with GUI Mods?

Kind regards

John

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@johnparVIC

I asked that question some time ago and was told that it is not possible.

It should be possible as it is with DC loads.

screen-shot-2022-10-03-at-23959-pm.png

In the system setup there is a question "Has DC system" and if you do not select it the "DC load" are not included in VRM.

Why not add a question "Has AC loads"?

2 Likes 2 ·
embtek-solar avatar image embtek-solar marekp commented ·
I would also appreciate being able to disable AC-Loads.


This is useful in following case:
  • 3 Phase victron system
  • Gridmeter counts only sum of all phases
  • Victron ESS is configured to ESS->Multiphase control = sum of all phases
  • No loads between Energymeter and AC-In of victron

Using the Victron inverters for metering consumption is not an option. Since in my country the grid meter counts only sum of all phases, Victron 3-phase system counts the consumption on each phase. So it is not forming a overall net from all phases, leading to wrong data in VRM.

3 Likes 3 ·
dognose avatar image dognose embtek-solar commented ·
Same Issue.


But well, there are "AC-Loads" (the meter and the NA-Protection) :P

0 Likes 0 ·