Is it possible to restart Quattro automatically using a generator after an overload?

In our three phase Quattro system, we have both grid power and generator power available. Sometimes when the grid power is connected, the power being used is more than the capacity of the inverter. When the grid switches off, the inverters can go into overload if the power being used is close to or exceeding the capacity of the inverters. The generator is automatically started in that situation, but the inverter will not restart because the error must be manually cleared. When it does restart, it starts in inverter mode and then changes to generator. Is it possible to configure the inverters to restart automatically in passthru mode after the generator has started? As it is, the generator is started but because the inverters cannot restart it just burns fuel doing nothing until the system is reset.

MultiPlus Quattro Inverter ChargerGeneratorgenerator auto start
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

once a inverter overloads 3 times you have to turn the on off switch off then back on. to clear the error

so unless you can do that by some sort of timer relay thats triggered on a generator start there is nothing you can do.

downside is if you did this is that there would be a power off and then on again every time the gen was started.


as far as I know anyway

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kw4np avatar image kw4np commented ·
@Paul B , It doesn't seem like the inverter is overloading three times, that may be another issue. Usually it happens when the grid switches off, and it doesn't seem to try three times. I've found that I can clear the error without using the switch with the remote console. Is there some way to program that to happen after an error code? Another problem is that the inverters always start first and switch to generator, I want the inverters to start in passthru mode to avoid the same overload situation.
0 Likes 0 ·