If I connect from mains power to charging socket with a 10a lead it trips mains power after about 5mins charging.
If i use my 15a lead it trips mains in a split second.
Any ideas?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
If I connect from mains power to charging socket with a 10a lead it trips mains power after about 5mins charging.
If i use my 15a lead it trips mains in a split second.
Any ideas?
You didn't say what your circuit breaker is rated at.
I don't know with how much power you are charging, but I'll assume it's maximum power ~3KW.
A 10A lead will have thinner wires and will offer some resistance and cause power to be lost as heat over its length. If your circuit breaker did not kick in after 5 minutes, the lead would most likely have melted since ~12A is going through it.
Your 15A lead will offer much less resistance to the circuit and allow the circuit breaker to do it's job more effectively.
A 5KVA MultiPlus is a heavy duty appliance and shouldn't be operated with mains leads. It should be properly installed with structured cabling and appropriate circuit protection.
The lead im connecting is from mains house feed into the victron via rated plugs and fuses & trips its a full pro install. My brother is a electrician but out at mines atm so no contact.
Hi Greg. That CCGX is handy. Go into it's Multiplus section and set the 'Input current limit' to 10A (say). Note that's in ac amps, so maybe 2300W. Your Multi is capable of accepting more than that of course, but you'd need to step up the breaker/wire size to handle it.
Oh ok cool i will have a look at that, its very handy indeed, nxt to workout the phone app. ;-) cheers will go have a look now.
JohnC cheers ok so should the AC input1 feed be 15amp if the supply is a 15amp plug?
When power coming in multicolour reads 10amp i get some photos i think yeh?