question

semlohnhoj avatar image
semlohnhoj asked

Does the Multi RS Solar feed in to the grid?

The Multi RS Solar has ESS options for "Optimise with/without battery life". When you use this, it uses the batteries first and any additional load requirement at the output is achieved by using the grid AC in feed.


My question is, will this result in any grid feed in either deliberately or just by leakage and is this allowed in the UK?


I don't want any grid feed in if that wasn't already obvious :)


I'm looking for some facts here rather than speculation or hypothesis if someone really knows the answer?

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

ESS (grid interaction) on the MultiRS Solar is currently not allowed in the UK because it is not type tested yet.
The IET would take their own time performing product type testing.

The MultiRS Solar can be used in it's default configuration as inverter / charger where it does not feed back.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

semlohnhoj avatar image semlohnhoj commented ·
Thanks for the quick response.


Under what circumstances would it feed back into the grid? Is it if the batteries are fully charged and there is excess solar available over and above an load requirement?


What I really want is self consumption without feed in.

0 Likes 0 ·
Show more comments