Is it possible to connect 6 units together in configuration two per phase ?
Are there any differences between MultiPlus, MultiPlus-II, Quattro, and Quattro-II ?
Goal is to provide redundancy in case of single unit failing.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is it possible to connect 6 units together in configuration two per phase ?
Are there any differences between MultiPlus, MultiPlus-II, Quattro, and Quattro-II ?
Goal is to provide redundancy in case of single unit failing.
Yes, apart from 8 and 10k multis which can’t be paralleled.
Read the spec sheets carefully and also the victron 3-phase and parallel system guide.
These are complex systems and best not done if the background and training is lacking.
Parallel does not provide redundancy.
If one unit in the system has an issue, they all go down.
You can however then manually change the configuration but this is not a configuration designed for redundancy.
Yes.
Redundancy is possible but not automatic.
If two fail you can reprogram system configuration for the remainning ones.
For example:
L1 1x, L2 2x, L3 1x
Thank you all for the answers. I was just looking for ability to keep 3 phases active until replacement arrives. Manual reconfiguration is sufficient. Having 2 units per phase already lowers probability of failure.