Hello, for a mobile application i use a Phoenix inverter 12/375.
It's connected to a VENUS GX which is connected to a Multiplus 48/3000 (the new one).
In this new car/van, the alternator always change the battery charging voltage. 80% of time it's more than 14v, but sometimes and it never last too longs (few second) the voltage go down near 12v.
Problem : i have configured the battery low cut-off to 12V, because it's the vehicule main battery and i don't want to discharge it. So Phoenix each time voltage goes down to 12v cut the inverter.
My question : Can i configure a timer in the phoenix to say it : if and only if the entry voltage goes down more than 30/60s than you cut the inverter. (you don't cut it if you have 11,8v for 1second for example)
I hope i was clear.
Thanks ;)
Best regards,
Emmanuel