I have setup grid feed-in limit to 0W and it still feeds in to more than 400 W. I tried to disable feed-in also, but still feeds-in as well at to 400 W.
What might be the problem?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have setup grid feed-in limit to 0W and it still feeds in to more than 400 W. I tried to disable feed-in also, but still feeds-in as well at to 400 W.
What might be the problem?
Try pulling some watts from the grid with a higher grid set point.
If it thinks it is trying to limit the export, and failing to do so, is there some problem with the current sensing e.g. an external current transformer or meter is connected the wrong way round, clamped round the wrong wire, or has a broken connection somewhere? Is this a new problem, or has it never worked correctly since installation?
Hello.
MultiPlus 24/3000/70-50 FW 497, CCGX 2.90, MPPT 150/70 VE.CAN FW2.05. MPPT 100/30 Ve.Direct , ABB PV Inverter on AC IN 2,5KW. Old time use CCGX with 2.33 FW, and all good, but no Grid Feed in limitation function. Today upgrade all FW, but very strange hapening. MPPT 150/70 VE CAN (OLD MODEL) power reducing to 0. MPPT with VE. DIRECT Working. No feed limit ON. If i downgrade CCGX to 2.33 FW, all works fine, but i need Feed IN limit to 4kw.
ThankYou for support
Best regard, Micius