I am trying to limit feed in power but with no success.
When I set limit to 0W or any other value:
System ignores the setting:
What I am doing wrong?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I am trying to limit feed in power but with no success.
When I set limit to 0W or any other value:
System ignores the setting:
What I am doing wrong?
Hi @MarekP,
My first guess would be the Fronius inverter is not prioritising the reduce output messages sent by the GX device - I would double check the configuration on the Fronius Inverter.
The specific instructions are here -
Perhaps post a screenshot of those settings as you see them if you believe they are correct.
Your guess was correct.
The setting were not correct. I assume they were at default.
My installer probably never touched them.
Good think he gave my the service password. :)
Thank you for a quick response to my question.
@Guy Stewart (Victron Community Manager)
I just remembered something.
"Feed limit active" was "Yes" only when "DC-coupled PV - feed on excess" was on.
When I turned "DC-coupled PV - feed on excess" OFF the "Feed limit active" was "No".
I cannot test it now because I do not remember the Fronius settings before I changed them.