Multiplus 24/1200/25 when the switch from generator is first turned on the Charger light flashes , tried leaving it a minute or two but continues to flash . Turn Multiplus off then to charger only without disconnecting generator and after 30 seconds which I assume is for it to synchronise it constant yellow and charging . Turn Multiplus off again then on to normal running position for Inverter/Charger and steady Yellow Light , constant charge .
Each time i use it for charging the first 30 minutes the output is erratic then settles down to steady Bulk Charge then Adsorption . All settings other than Voltage set-points are default .
The Multiplus doesn't appear to be regulating from the Cerbo Temperature Sensor . The DVCC is on and shared Temperature sense is selected but not the shared Voltage sense as I think the Multiplus gets its own from the Busbar but the VE Bus Summary shown the Multiplus is going from Bulk to Absorption at the Voltage set points and not at a lower Temperature compensated voltage .