Disappointed to see a supposed CCL of 148Amp on 4 x Pylontech US3000C limited to 50Amps with batteries at 18°C - 19°C It says in the manual Here that it should charge to the CCL limit which is controlled by DVCC but this is not my experience with a MultiPlus 5kW and 7kW generator. Is there a problem with this paragraph in the manual or something wrong with my installation?
"You can confirm if this is affecting your installation be entering the Pylontech Battery menu on your GX device, and then the Parameters Menu. This will report the Charge Current Limit (CCL) and Discharge Current Limit (DCL). "