Multiplus: gen start on low SOC

Multiplus with CCGX and BVM 700. Generator does not start when conditions for low SOC, set on CCGX, are correct. The BVM menu on the CCGX does not show a value for SOC, but the Multiplus menu on CCGX does show a SOC value. But the setting 'Synchronize VE.Bus SOC with battery' is unchecked. Should this be checked? Or is there another problem?

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

Yes, tick this box, it will make the BMV the master SOC source.

https://www.victronenergy.com/live/ccgx:start