HI < I have the following installed and working ok until a recent shift in the weather so needed the generator,
1 x 10KW Quattry with 433 firmware updaed
Color GX with V2,23
2 x MPPT 150/100 with V1,39 ( 24 x 250Watt modules)
BYD Box 10 x 2 with V4.17
Good quality 1500RPM 15KVA Generator with very stable 231V output and 51HZ no reaction to loads( IE no slowing etc)
System has been working fantastically well under quite heavy loads until called for generator,
The system starts generator ok on demand at an SOC of 20%, and runs up genny ok, then connects to the Quattro input and goes through the normal sequence, starts bulk charge, after a few mins ( even as much as 15 mins) all seems normal, then for no apparent reason the AC input is dropped by the inverter, and the system reverts to invert, after a few minutes the AC in accepts input and goes to passthrough and then Bulk, and again after a few mins drops the AC input, and so it goes on,l imit inverter off,
On system Setup,
Battermonitor automatic, Sync VE BUS SOC On,/use solar charger current to improve Bus VE SOC on, Solar charger voltage control On, Solar charger current control on,Has DC System off, DVCC On, , SVS Off, STS On, Limit charge current On, BMS control On
Generator start stop, on Auto, SOC< Battery voltage and Load atr 5KW,
any ideas as to why the Inverter keeps dropping AC would be helpful, or if I have any setting incorrect or not activated please advise,
thanks,